    Novice
    Novice
    Jason 7/25/2011 4:25 PM

    This morning the UPS faulted and all the server rebooted, once the ups came back up I checked the properties page and I see that there is a battery fault and an alert (see attached picture). I click on the alert and I see this:

    11 2011/07/25 07:56:35 Battery Fault
    12 2011/07/25 07:56:37 No Battery
    13 2011/07/25 07:56:37 Replace Battery
    14 2011/07/25 07:56:37 Unavailable Battery

    but on the properties page (see attached picture) under battery status it says the battery is fully charged and the last periodic test was ok.

    What is the ups telling me? Do I need to replace the battery, or the whole system?

    Thanks,

    Jason

    Attachments
  • R2
    Rob
    =S= Representative
    Rob 7/26/2011 7:51 PM (in response to Jason)

    Hi mpeeng, the MGE pulsar is a single phase MGE ups which has been taken over by Eaton. You should be able to contact them at 1 800 356 5794 for further assistance. Hope this helps.

  • Olin
    Olin
    Novice
    Novice
    Olin 7/28/2011 12:10 PM (in response to Jason)

    Sounds most likely just a faulty battery, how old is it? What's the ambient temp? Is it discharged/tested often?

  • mpeeng
    Jason
    Novice
    Novice
      This discussion is marked as answered
    Jason 7/28/2011 2:10 PM (in response to Olin)

    The batteries are 4 years old and the ambient temp is around 17-20 degrees Celsius.

    I believe the fault may be with the extra external battery (A MGE Pulsar EXB 2200/3200) but I can't figure out how to remove the battery from there. I think I may hace to disconnect the whole EXB unit. Is it safe to do that while the ups is running?

  • Olin
    Olin
    Novice
    Novice
    Olin 7/28/2011 7:15 PM (in response to Jason)

    Well the temp is good but even at that 4 years is about end of useful life for the small batteries in them. Should be ok to disconnect if you still have internal batteries and the system is not on battery.