Printer on UPS (8 Hrs backup)

Discussion in Smart-UPS & Symmetra LX / RM started by Jitu , 9 days ago
Login to follow, share, and participate in this space.
Not a member?Join now
  • jninan
    Jitu
    New Member New Member
    Jitu 9 days ago

    Hi All,

    I would like to know which UPS can run a printer (50 W) for 8 hrs without charging. I have been trying many different models and i am not sure if I am doing the right way. 1000 VA Smart UPS gives me around 4 hrs. So is 2000 VA the best choice I have to double the backup time? 

    Or is there another series of UPS intended for long hours of back up run time for mobile solutions ?

  • RichScreen
    Richard
    =S= Representative
    Richard 9 days ago (in response to Jitu)

    Hi Jitu,

     

    If you navigate to apc.com and select your Country

    Then navigate to:

    Support > Resources & tools > Tools & selectors

    Then select “UPS Selector”

     

    If you enter the expected load the tool will recommend a solution.

     

    Regards

    Rich…

    Richard, UK Advanced Technical Support
  • UnexpectedBill
    William
    Apprentice Apprentice
    William 8 days ago (in response to Jitu)

    What you probably want is a Smart-UPS with the extended runtime (XL) option and a few battery boxes.

    If this is a laser printer, it's worth considering that the inrush current may exceed the inverter's capabilities in even a fairly large UPS.

    There are some Back-UPS products with limited extended runtime capability. You would have to be sure that your printer is OK with modified sine wave power if you chose a Back-UPS model.