Discussion in Smart-UPS & Symmetra LX / RM started by Ken , 7/10/2017 6:30 PM
Login to follow, share, and participate in this space.
Not a member?Join now
  • ksquare
    Ken
    Novice Novice
    Ken 7/10/2017 6:30 PM

    The LX Powerview display shows PM operating temperature. What is a safe maximum temperature?

  • RichScreen
    Richard
    =S= Representative
    Richard 7/11/2017 3:07 PM (in response to Ken)

    Hi Ken

     

    Based on the power module (SYPM4KI) product page on apc.com

    http://www.apc.com/shop/uk/en/search?Dy=1&Nty=1&Ntt=SYPM4KI

     

    I see in the “Technical Specifications” tab under Environmental;

    Operating environment 0 to 40 degrees C

    Operating relative humidity 0 to 95%RH

    Storage temperature -15 to 45 degrees C

    Storage relative humidity 0 to 95%RH

     

    Regards,

    Rich…

     

    Richard, UK Advanced Technical Support
  • ksquare
    Ken
    Novice Novice
    Ken 7/12/2017 5:47 PM (in response to Richard)

    Duh, I guess I should have found that. I'm getting lazy :-) Thanks!

  • RichScreen
    Richard
    =S= Representative
      This discussion is marked as answered
    Richard 7/13/2017 8:03 AM (in response to Ken)

    Hi Ken,

     

    Your very welcome.

     

    Rich…

    Richard, UK Advanced Technical Support