Loading ...
home » spaces » Smart-UPS & Symmetra LX / RM » discussion » General » Smart UPS 2200 - No Power

Smart UPS 2200 - No Power

Discussion in Smart-UPS & Symmetra LX / RM started by Wizz , 4/13/2009 5:22 PM
Login  to follow, share, and participate in this space.
Not a member?Join now
  • Wizzkidy
    Wizz
    New Member
    New Member
    Wizz 4/13/2009 5:22 PM

    Hi, I have an old rack mountable Smart-UPS 2200 the serial numbers on the back are posted below:

    S/N - DL2200RMI3U
    GD0040008308

    The problem I have is the thing won't power up, The battery itself looks brand new but I checked the battery on a meter and it had very little charge (something like 2 - 3V in it)

    I thought the UPS would charge the battery but I have left it in the unit plugged in for awhile with no joy. Does this battery need to be charged before the unit will turn on? I have had the UPS open and cannot see anything burnt out, its just I get no power when plugged in.

    Is there any way of finding out this UPS works without charge in the battery? I would rather not spend out on a new battery if the UPS turns out to be dead.

    Also if the battery is dead, How much will I be looking at for a replacement?

    Thanks

  • ipicKedawinna
    Angela
    =S= Representative
    Angela 4/13/2009 10:45 PM (in response to Wizz)

    hi

    this particular model will not turn on without good DC voltage.

    take a look at [this thread|http://forums.apc.com/spaces/5/smart-ups-symmetra-lx-rm/forums/general/4334/smartups-3000-repairable/1#16307] for use at your own discretion but i'd recommend trying a new set of batteries to get it to power on.

  • Wizzkidy
    Wizz
    New Member
    New Member
    Wizz 4/15/2009 4:33 PM (in response to Wizz)

    Hi thanks for that.

    I managed to get my hands on one charged battery pack, the unit won't power on still though, Does this unit need two battery packs to start up? I ask because inside the unit it has two connectors for two packs, I presume it needs both and not just one pack?

    Message was edited by: Wizzkidy

  • ipicKedawinna
    Angela
    =S= Representative
    Angela 4/15/2009 5:49 PM (in response to Wizz)

    i confirmed on this end that it will require both batteries to turn on or else it wont be a complete circuit.

  • Wizzkidy
    Wizz
    New Member
    New Member
    Wizz 5/4/2009 1:47 PM (in response to Wizz)

    Hi again,

    I thought I would update my thread, I managed to get another battery and now the UPS works without a problem, It seems a little overkill for my living room though :) I kinda have my Server/Gaming machine monitor cable modem switch and some other small bits on it, it barely has 1 bar of load 0_0

    The only issue I have is that it didn't come with a Serial cable to connect the UPS up, Does anyone have a spare one of these lying about? and if so would they mind posting it off :D? if not which cable do I need ? :/

    Thanks.

  • ipicKedawinna
    Angela
    =S= Representative
    Angela 5/4/2009 5:33 PM (in response to Wizz)

    you will need [one of these|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=940-0024] or the 940-1524 15 foot version which you may be able to grab.

    i am sure you may be able to find one some place else though

  • Page 1 of 1 (6 items)
powered by Communifire
Version 5.0.5741.40378
Choose your language:  English