server doesnt power off and i cant change percentage

Discussion in Back-UPS & Surge Protectors started by Mauro , 12 days ago
Login to follow, share, and participate in this space.
Not a member?Join now
  • mmiat
    Mauro
    New Member New Member
    Mauro 12 days ago

    hi

    i've a (usbterm output):

    Name: Back-UPS RS 900G FW:879.L4 .I USB FW:L4
    Serial #: 3B1345X22334
    the server doesnt shut down when the battery is exhausted
    i tried to change percentage of battery management, and i cant, it simply return to 5%, no advice/alert of any type
    i tried to reset/change/restart, nothing changes
    i tried to install power chute business edition, i downloaded 9.5 versione, completely different from which i used in the past, is not a software but an agent, i have to access through browser and it cant see my ups
    i tried to modify permissions in HKEY_LOCAL_MACHINE\SYSTEM\ControlSet001\Control\Power\User\PowerSchemes, nothing changes
    i tried using powercfg.exe, but i'm not sure what i've to do
    any help?
    thanks
  • wpasquil
    Bill
    =S= Representative
    Bill 11 days ago (in response to Mauro)

    Hi,

    PowerChute Business Edition is not compatible with a Back-UPS. If you would like to run PowerChute you will need to install PowerChute Personal Edition. 

    If you want to use the native power option please review Schneider Electric FAQs  FA159653 and FA159743

  • mmiat
    Mauro
    New Member New Member
    Mauro 8 days ago (in response to Bill)

    PowerChute Personal Edition runs on windows server?

  • wpasquil
    Bill
    =S= Representative
    Bill 4 days ago (in response to Mauro)

    Hi,

    PowerChute Personal Edition is not officially supported on Windows Server however it should run. Another option you have is to install APCUPSD. APCUPSD is a third party application. 