APC XS 1300 will not turn on - beeps while the button is held down

Discussion in Back-UPS & Surge Protectors started by John , 14 days ago
Login to follow, share, and participate in this space.
Not a member?Join now
  • jgloor
    John
    New Member New Member
    John 14 days ago

    I had a power outage - after which, the APC XS 1300 would not power on.

    I have replaced the batteries, now when I hold down the power button - the unit beeps as long as it's held down.  It does not power on. (Everything has been disconnected, tried on different power outlets, checked the breaker, removed the batteries - waited an hour and tried again.) 

    I have bought a new unit (same one - xs1300)  would like to get the old one working again, any suggestions?

    Thanks,

    John

  • RandyH
    Randy
    Novice Novice
    Randy 13 days ago (in response to John)

    Do you happen to own a meter for testing the voltage of the new battery?

    It should be at least 25.2v...... or more

    Try pressing the RESET button.

    Are you sure you inserted the battery pack correctly?

  • jgloor
    John
    New Member New Member
    John 12 days ago (in response to Randy)

    Tested the battery - it's showing 24.5 volts (My meter is out of calibration... show -1.2 when not connected... old meter)

    Pressed the reset button.

    Checked all of the connection - they are OK.