Battery Icon empty and flashing

Discussion in Back-UPS & Surge Protectors started by Daniel , 7/13/2017 4:29 PM
Login to follow, share, and participate in this space.
Not a member?Join now
  • powerpc
    New Member New Member
    Daniel 7/13/2017 4:29 PM

    I purchased a used BR1500G on ebay with no batteries and put in a APCRBC124 that was about 4 months old and when I turn it on it doesn't perform a self test and the battery icon just flashes. I don't think it knows there is a battery plugged in. The battery icon flashes as seen in the attachment and after an hour nothing had changed. When I measured the voltage on the battery pack yesterday, it was either 25 or 28 volts. It also came with some kind of divider with a cable, I guess if my battery pack was not "taped" together I might need that but I'm not using it because the battery pack slides right in. Thanks for any help anyone can provide.

  • wpasquil
    =S= Representative
    Bill 7/17/2017 7:15 PM (in response to Daniel)


    The battery pack should be wired in series and should read around 26 27 volts DC when good. 

    Here are a few images of the battery pack when connected properly