Loading ...
Home » Spaces » Back-UPS & Surge Protectors » discussion » General » Input Power Wattage for SURT6000RMXLI

Input Power Wattage for SURT6000RMXLI

Discussion in Back-UPS & Surge Protectors started by Jaylen , 4/17/2017 9:15 AM
Login to follow, share, and participate in this space.
Not a member?Join now
  • zone85
    Jaylen
    Novice Novice
    Jaylen 4/17/2017 9:15 AM

    Can anyone help regarding this? I am not able to get this information from the specification sheet of the UPS.

  • zone85
    Jaylen
    Novice Novice
    Jaylen 4/17/2017 9:18 AM (in response to Jaylen)

    I will like to know the power consumption at charging and idling. Thanks in advance! =)

  • Nicole
    Nicole
    =S= Representative
    Nicole 4/18/2017 4:23 PM (in response to Jaylen)

    Hi Jaylen, 

    The internal consumption of this UPS at full load with the batteries fully charged is 336W. The power consumption of this UPS at full load with fully discharged batteries is 757W. 

    Let me know if you have any other questions, 

    Nicole 

  • zone85
    Jaylen
    Novice Novice
      This discussion is marked as answered
    Jaylen 4/19/2017 12:57 AM (in response to Nicole)

    Noted. That's all I need. Thanks! =)

  • Page 1 of 1 (4 items)
Choose your language:  
powered by Communifire
Version 5.2.6420.11692