Loading ...
home » spaces » NetBotz Hardware & Software » discussion » General » APC Alarm Beacon Options for Multiroom Alerts

APC Alarm Beacon Options for Multiroom Alerts

Discussion in NetBotz Hardware & Software started by alec , 5/1/2012 8:24 PM
Login  to follow, share, and participate in this space.
Not a member?Join now

Note: No new discussion posts are allowed in this area. Historical content is for viewing purposes only. NetBotz are actively supported at its own standalone community - http://dcimsupport.apc.com

  • Alec
    New Member
    New Member
    alec 5/1/2012 8:24 PM

    New to APC. Just brainstorming ideas on how to use the products. If it is possible or not.

    Can alerts on one NetBotz trigger another NetBotz to turn on its beacon?

    Pretty much.. if someone opens a rack in room 1. the main control center in room 2, will have its beacon light turn on alerting people to go look who is in room 1.

    Or would have to rely on text alerts ?

  • TaSpEc
    Andrew 5/2/2012 2:08 PM (in response to alec)

    Its a little convoluted, but yes its possible. Basically the customer would need to connect the netbotz dry contact cable (nbes0304) from the 450/550 netbot in room 2 to the output relay ports on the 450/550 in room 1. Then configure the door threshold to trigger a state change on the output relay. The dry contact threshold on the netbot in room 2 would then need to be configured to trigger the beacon alert action when there was a state change.

    So door opens-->triggers output relay to change state-->dry contact sees this state change-->triggers beacon.

    Be aware that if power is cycled on a netbot 200/450/550, the relay contacts change state as part of its start up diagnostics. Also the maximum supported distance of the netbotz dry contact cable is 100 ft using cat5 extensions.

    Message was edited by: TaSpEc

  • Page 1 of 1 (2 items)
Choose your language:  English  
powered by Communifire
Version 5.0.5741.40378