Loading ...
home » spaces » NetBotz Hardware & Software » discussion » General » Camera Pod Problem

Camera Pod Problem

Discussion in NetBotz Hardware & Software started by Wesley , 7/25/2013 9:19 PM
Login  to follow, share, and participate in this space.
Not a member?Join now
Announcement 

Note: No new discussion posts are allowed in this area. Historical content is for viewing purposes only. NetBotz are actively supported at its own standalone community - http://dcimsupport.apc.com

  • wesross
    Wesley
    Novice
    Novice
    Wesley 7/25/2013 9:19 PM

    Ok, I'm having an issue with some Camera pods. I have a netbotz 570. I have 3 camera pod 160s connected via USB. One of the 3 camera's constantly disconnects then reconnects then disconnects then reconnects over and over and over. They are all connected by USB Extentions. I have replaced the cable, the camera, and even the netbotz has been replaced but this issue continues. Any suggestions?

  • ipicKedawinna
    Angela
    =S= Representative
    Angela 7/30/2013 4:07 PM (in response to Wesley)

    vsales - is this something you could help with?

  • caguzmanj
    Carlos
    Novice
    Novice
    Carlos 8/7/2013 10:22 PM (in response to Wesley)

    Netbotzhavethelogs?. Ifyou could findthe timeyou checkbeforeyoudeseconectenthe cameras andtry to avoidorresolve

  • breda1311
    Breda
    =S= Representative
    Breda 8/8/2013 3:43 PM (in response to Wesley)

    Hello,

    It is possible to get the logs from the Netbotz appliance please? The appliance log and the application event logs?

    What are the frame rates/resolution on all 3 cameras? Are they the same? You might need to reduce the frame rate on the camera that is causing a problem and reboot and see if this helps the situation.

    How often is this happening? Is there a lot of motion being detected on this camera moreso then the other cameras?

    Does a reboot of the appliance help?

    What is the Botzware that is running on the unit?

    Is there anything else connected to the appliance besides the 3 cameras?

  • wesross
    Wesley
    Novice
    Novice
    Wesley 8/8/2013 6:27 PM (in response to Breda)

    all there are running 640x480 at 5 frames/sec. it was higher and I have rebooted the netbotz many times but that has no affect at all.  The issue is constant. Connecting and disconnecting over and over ever few seconds.

    the application version is 4.2.0

    There are six regular sensors also plugged into the netbotz also.

  • breda1311
    Breda
    =S= Representative
    Breda 8/9/2013 8:00 AM (in response to Wesley)

    Hi,

    What USB extension cable are you using? Whats the SKU?

    What is the distance from the Netbotz unit to camera 1, to camera 2 and to camera 3?

    The max distance allowed is 80 feet, but this is with repeaters and hubs to boost the signal.

    Is it possible to send in the logs to further troubleshoot?

    Regards,

    B

  • wesross
    Wesley
    Novice
    Novice
    Wesley 8/13/2013 6:11 PM (in response to Breda)

    They are from Monoprice. http://www.monoprice.com/products/product.asp?c_id=103&cp_id=10303&cs_id=1030312&p_id=7644&seq=1&format=2

    82ft USB active extension repeater cable. All three are using the exact same cable, the same length. Only one is having the issue.

    Log:

    Aug 13 11:07:44 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:07:44 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:07:49 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:07:50 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:07:50 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:08:10 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:08:10 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:08:15 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:08:15 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:08:20 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:08:20 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:08:20 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:08:25 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:08:25 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:08:30 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:08:30 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:08:36 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:08:36 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:08:51 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:09:22 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:09:53 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:10:24 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:10:55 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:11:10 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:11:10 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:11:15 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:11:15 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:11:20 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:11:20 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:11:26 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:11:26 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:11:26 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:11:28 netbotz9E868A daemon.err nbSendHTTPReport: Error posting to url http://192.168.1.1:80/botpost/sensor: HTTP code=401, err=22

    Aug 13 11:11:28 netbotz9E868A daemon.err nbSendHTTPReport: All URLs failed

    Aug 13 11:11:58 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:12:06 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:12:06 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:12:11 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:12:11 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:12:16 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:12:16 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:12:21 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:12:21 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:12:29 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:13:00 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:13:31 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:13:57 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:13:57 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:14:02 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:14:02 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:14:02 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:14:07 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:14:07 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:14:13 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:14:13 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:14:33 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:14:42 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:14:42 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:14:47 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:14:47 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:14:52 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:14:52 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:14:58 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:14:58 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:15:04 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:15:10 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:15:10 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:15:15 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:15:15 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:15:20 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:15:20 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:15:26 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:15:26 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:15:36 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:16:07 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:16:38 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:17:09 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:17:40 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:18:11 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:18:42 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:19:14 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:19:41 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:19:41 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:19:45 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:19:46 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:19:46 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:19:51 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:19:51 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:19:56 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:19:56 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:20:08 netbotz9E868A daemon.info thttpd[2256]: up 428400 seconds, stats for 3600 seconds:

    Aug 13 11:20:08 netbotz9E868A daemon.info thttpd[2256]:   thttpd - 1447 connections (0.401944/sec), 1 max simultaneous, 36175000 bytes (10048.6/sec), 6 httpd_conns allocated

    Aug 13 11:20:08 netbotz9E868A daemon.info thttpd[2256]:   libhttpd - 82 strings allocated, 19200 bytes (234.146 bytes/str)

    Aug 13 11:20:08 netbotz9E868A daemon.info thttpd[2256]:   map cache - 3 allocated, 0 active (0 bytes), 3 free; hash size: 1024; expire age: 1800

    Aug 13 11:20:08 netbotz9E868A daemon.info thttpd[2256]:   fdwatch - 5077 selects (1.41028/sec)

    Aug 13 11:20:08 netbotz9E868A daemon.info thttpd[2256]:   timers - 3 allocated, 3 active, 0 free

    Aug 13 11:20:16 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:20:34 netbotz9E868A local0.debug dhcpcd[1103]: sending DHCP_REQUEST for 192.168.0.206 to 192.168.1.1

    Aug 13 11:20:34 netbotz9E868A local0.debug dhcpcd[1103]: dhcpIPaddrLeaseTime=3600 in DHCP server response.

    Aug 13 11:20:34 netbotz9E868A local0.debug dhcpcd[1103]: dhcpT1value is missing in DHCP server response. Assuming 1800 sec

    Aug 13 11:20:34 netbotz9E868A local0.debug dhcpcd[1103]: dhcpT2value is missing in DHCP server response. Assuming 3150 sec

    Aug 13 11:20:34 netbotz9E868A local0.debug dhcpcd[1103]: DHCP_ACK received from  (192.168.1.1)

    Aug 13 11:20:47 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:21:00 netbotz9E868A syslog.info -- MARK --

    Aug 13 11:21:08 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:21:08 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:21:12 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:21:12 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:21:13 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:21:13 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:21:17 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:21:17 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:21:18 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:21:18 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:21:18 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:21:22 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:21:22 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:21:23 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:21:23 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:21:27 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:21:27 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:21:28 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:21:28 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:21:29 netbotz9E868A daemon.err nbSendHTTPReport: Error posting to url http://192.168.1.1:80/botpost/sensor: HTTP code=401, err=22

    Aug 13 11:21:29 netbotz9E868A daemon.err nbSendHTTPReport: All URLs failed

    Aug 13 11:21:32 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:21:32 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:21:49 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:22:05 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:22:05 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:22:10 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:22:10 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:22:15 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:22:15 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:22:20 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:22:20 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:22:20 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:22:23 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:22:23 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:22:25 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:22:25 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:22:28 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:22:28 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:22:30 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:22:30 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:22:33 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:22:33 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:22:35 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:22:35 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:22:39 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:22:39 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:22:41 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:22:41 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:22:44 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:22:44 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:22:49 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:22:49 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:22:51 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:22:54 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:22:54 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:23:23 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:23:32 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:23:32 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:23:37 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:23:37 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:23:42 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:23:42 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:23:48 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:23:48 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:23:54 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:24:25 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:24:29 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:24:29 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:24:34 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:24:34 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:24:39 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:24:39 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:24:44 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:24:44 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:24:50 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:24:50 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:24:56 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:25:00 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:25:00 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:25:05 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:25:05 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:25:10 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:25:10 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:25:16 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:25:16 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:25:27 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:25:58 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:26:29 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:27:01 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:27:32 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:28:03 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:28:06 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:28:06 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:28:11 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:28:11 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:28:16 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:28:16 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:28:22 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:28:22 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:28:34 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:29:05 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:29:32 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:29:32 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:29:36 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:29:37 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:29:37 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:29:42 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:29:42 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:29:48 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:29:48 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:30:07 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:30:38 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:31:10 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:31:21 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:31:21 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:31:26 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:31:26 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:31:28 netbotz9E868A daemon.err nbSendHTTPReport: Error posting to url http://192.168.1.1:80/botpost/sensor: HTTP code=401, err=22

    Aug 13 11:31:28 netbotz9E868A daemon.err nbSendHTTPReport: All URLs failed

    Aug 13 11:31:31 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:31:31 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:31:36 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:31:36 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:31:41 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:31:42 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:31:42 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:31:46 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:31:46 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:31:51 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:31:51 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:31:56 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:31:56 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:32:02 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:32:02 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:32:12 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:32:33 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:32:33 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:32:38 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:32:38 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:32:43 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:32:43 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:32:43 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:32:49 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:32:49 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:33:09 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:33:09 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:33:14 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:33:14 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:33:14 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:33:19 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:33:19 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:33:24 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:33:24 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:33:45 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:33:47 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:33:47 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:33:52 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:33:52 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:33:57 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:33:57 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:34:02 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:34:02 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:34:16 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:34:47 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:35:19 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:35:41 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:35:41 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:35:45 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:35:45 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:35:50 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:35:51 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:35:51 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:35:56 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:35:56 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:36:21 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:36:52 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:37:23 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:37:54 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:38:25 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:38:56 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:39:28 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:39:59 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:40:30 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:41:00 netbotz9E868A syslog.info -- MARK --

    Aug 13 11:41:01 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:41:28 netbotz9E868A daemon.err nbSendHTTPReport: Error posting to url http://192.168.1.1:80/botpost/sensor: HTTP code=401, err=22

    Aug 13 11:41:28 netbotz9E868A daemon.err nbSendHTTPReport: All URLs failed

    Aug 13 11:41:32 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:41:59 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:41:59 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:42:03 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:42:04 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:42:04 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:42:09 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:42:09 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:42:15 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:42:15 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:42:34 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:43:05 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:43:17 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:43:17 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:43:22 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:43:22 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:43:27 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:43:27 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:43:32 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:43:32 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:43:37 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:44:08 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:44:39 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:45:10 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:45:13 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:45:13 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:45:18 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:45:18 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:45:23 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:45:23 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:45:29 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:45:29 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:45:41 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:46:06 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:46:06 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:46:11 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:46:11 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:46:12 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:46:16 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:46:16 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:46:22 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:46:22 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:46:41 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:46:41 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:46:43 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:46:46 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:46:46 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:46:51 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:46:51 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:46:56 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:46:56 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:47:14 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:47:46 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:48:17 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:48:48 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:49:19 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:49:50 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:50:07 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:50:07 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:50:12 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:50:12 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:50:17 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:50:17 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:50:21 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:50:22 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:50:22 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:50:30 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:50:30 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:50:34 netbotz9E868A local0.debug dhcpcd[1103]: sending DHCP_REQUEST for 192.168.0.206 to 192.168.1.1

    Aug 13 11:50:34 netbotz9E868A local0.debug dhcpcd[1103]: dhcpIPaddrLeaseTime=3600 in DHCP server response.

    Aug 13 11:50:34 netbotz9E868A local0.debug dhcpcd[1103]: dhcpT1value is missing in DHCP server response. Assuming 1800 sec

    Aug 13 11:50:34 netbotz9E868A local0.debug dhcpcd[1103]: dhcpT2value is missing in DHCP server response. Assuming 3150 sec

    Aug 13 11:50:34 netbotz9E868A local0.debug dhcpcd[1103]: DHCP_ACK received from  (192.168.1.1)

    Aug 13 11:50:35 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:50:35 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:50:40 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:50:40 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:50:45 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:50:45 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:50:52 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:51:16 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:51:16 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:51:21 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:51:21 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:51:24 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:51:26 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:51:26 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:51:28 netbotz9E868A daemon.err nbSendHTTPReport: Error posting to url http://192.168.1.1:80/botpost/sensor: HTTP code=401, err=22

    Aug 13 11:51:28 netbotz9E868A daemon.err nbSendHTTPReport: All URLs failed

    Aug 13 11:51:31 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:51:31 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:51:53 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:51:53 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:51:55 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:51:58 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:51:58 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:52:03 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:52:03 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:52:09 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:52:09 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:52:20 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:52:20 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:52:25 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:52:25 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:52:26 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:52:30 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:52:30 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:52:35 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:52:35 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:52:38 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:52:38 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:52:43 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:52:43 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:52:48 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:52:48 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:52:54 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:52:54 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:52:57 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:53:10 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:53:10 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:53:15 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:53:15 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:53:20 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:53:20 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:53:26 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:53:26 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:53:28 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:53:59 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:54:05 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:54:05 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:54:10 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:54:10 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:54:15 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:54:15 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:54:21 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:54:21 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:54:30 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:54:34 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:54:34 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:54:39 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:54:39 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:54:44 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:54:44 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:54:50 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:54:50 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:55:01 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:55:33 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:55:36 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:55:36 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:55:41 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:55:41 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:55:46 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:55:46 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:55:51 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:55:51 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:56:04 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:56:35 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:57:06 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:57:26 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:57:26 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:57:29 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:57:29 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:57:31 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:57:31 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:57:34 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:57:34 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:57:36 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:57:36 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:57:37 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:57:39 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:57:39 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:57:42 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:57:42 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:57:44 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:57:44 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:58:07 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:58:07 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:58:08 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:58:12 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:58:12 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:58:17 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:58:17 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:58:23 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:58:23 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:58:39 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:59:10 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 11:59:11 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:59:11 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:59:16 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:59:16 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:59:21 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:59:21 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:59:26 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 11:59:26 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 11:59:42 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 12:00:01 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:00:01 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:00:06 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:00:06 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:00:11 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:00:11 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:00:13 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 12:00:16 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:00:16 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:00:44 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 12:01:00 netbotz9E868A syslog.info -- MARK --

    Aug 13 12:01:11 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:01:11 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:01:15 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 12:01:16 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:01:16 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:01:21 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:01:21 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:01:26 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:01:26 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:01:28 netbotz9E868A daemon.err nbSendHTTPReport: Error posting to url http://192.168.1.1:80/botpost/sensor: HTTP code=401, err=22

    Aug 13 12:01:28 netbotz9E868A daemon.err nbSendHTTPReport: All URLs failed

    Aug 13 12:01:46 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 12:02:00 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:02:00 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:02:05 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:02:05 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:02:10 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:02:10 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:02:15 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:02:15 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:02:17 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 12:02:35 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:02:35 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:02:40 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:02:40 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:02:45 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:02:45 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:02:48 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 12:02:50 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:02:50 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:03:19 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 12:03:51 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 12:04:10 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:04:10 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:04:15 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:04:15 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:04:20 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:04:20 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:04:22 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 12:04:25 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:04:25 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:04:26 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:04:26 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:04:30 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:04:30 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:04:35 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:04:35 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:04:40 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:04:40 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:04:53 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 12:05:24 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 12:05:39 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:05:39 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:05:43 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:05:43 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:05:49 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:05:49 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:05:54 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:05:54 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:05:55 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 12:06:00 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:06:00 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:06:05 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:06:05 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:06:10 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:06:10 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:06:13 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:06:13 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:06:16 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:06:16 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:06:18 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:06:18 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:06:23 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:06:23 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:06:26 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 12:06:26 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:06:26 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:06:28 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:06:28 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:06:31 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:06:31 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:06:33 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:06:33 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:06:36 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:06:36 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:06:42 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:06:42 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

    Aug 13 12:06:57 netbotz9E868A daemon.err nbAlinkDaemon: Received sensor value for non existent sensor for nbAlinkEnc_3 port 6

    Aug 13 12:07:19 netbotz9E868A daemon.err nbSurveilMgr: Error posting to url http://192.168.1.1:80/botpost/surveillance: HTTP code=401, err=22

    Aug 13 12:07:19 netbotz9E868A daemon.err nbSurveilMgr: All URLs failed

  • breda1311
    Breda
    =S= Representative
    Breda 8/14/2013 9:48 AM (in response to Wesley)

    Hi,

    We recommend using the Netbotz USB extension cable.

    The max that is supported is 80ft. That is the limit.

    Can you tell me the distance using for the following please:

    Appliance to camera 1?

    Appliance to camera 2?

    Appliance to camera 3?

    Can you as a test using a shorter cable without the repeaters for the camera that is having the issue please?

    Can you also test using just 2 cameras in the appliance, the problematic one and another one? Do you get the same results using just 2 cameras?

    Just to clarify you have the 3 cameras connected to a single USB port on the appliance? No hubs etc?

    Do you have another Netbotz onsite where you could test this camera?

    Regards,

    B

  • Page 1 of 1 (8 items)
Choose your language:  English  
powered by Communifire
Version 5.0.5741.40378